+1 vote
58 views
ago in TyphoonSim by lutz erhartt (16 points)
Bad voltage loop consisting of Idc, Three Phase Inverter1, Vs1 detected. The Basic Electrical.Short Circuit: Three Phase Inverter1.Im_short_dc inside Three Phase Inverter1 is degenerated, for the switch permutation (1 1 1 1 1 1).

Three Phase Inverter modell settings: Internal modulator and fixed carrier frequency, according to the basics tutorial

1 Answer

+2 votes
ago by Jovan Zelic (302 points)
selected ago by Debora Santo
 
Best answer
That warning tells you that, in case you short-circuit the inverter (switch permutation where all switches are closed), you will have a topological conflict between the switches and the voltage source of the DC link. Since you will probably never short-circuit your inverter, that will never actually happen. If you want to remove that ugly warning, you can just place some resistor in series with the voltage source. Even 1uOhm will remove the warning.
...